Digital Testing of High Voltage Circuit Breaker
Post: #1

INTROUCTION



ESSENTIAL QUALITIES OF HV CIRCUIT BREAKER

High-voltage circuit breaker play an important role in transmission and distribution systems. They must clear faults and isolate faulted sections rapidly and reliably. In-short they must possess the following qualities.

" In closed position they are good conductors.
" In open position they are excellent insulators.
" They can close a shorted circuit quickly and safely without unacceptable contact erosion.
" They can interrupt a rated short-circuit current or lower current quickly without generating an abnormal voltage.

The only physical mechanism that can change in a short period of time from a conducting to insulating state at a certain voltage is the arc.

With the advancement of power system, the lines and other equipment operate at very high voltages and carry large currents. High-voltage circuit breakers play an important role in transmission and distribution systems. A circuit breaker can make or break a circuit, either manually or automatically under all conditions viz. no-load, full-load and short-circuit conditions. The American National Standard Institute (ANSI) defines circuit breaker as: "A mechanical switching device capable of making, carrying and breaking currents under normal circuit conditions and also making, carrying for a specified time, and breaking currents under specified abnormal circuit conditions such as those of short circuit". A circuit breaker is usually intended to operate infrequently, although some types are suitable for frequent operation.


HISTORY

The first circuit breaker was developed by J.N. Kelman in 1901. It was the predecessor of the oil circuit breaker and capable of interrupting a short circuit current of 200 to 300 Ampere in a 40KV system. The circuit breaker was made up of two wooden barrels containing a mixture of oil and water in which the contacts were immersed. Since then the circuit breaker design has undergone a remarkable development. Now a days one pole of circuit breaker is capable of interrupting 63 KA in a 550 KV network with SF6 gas as the arc quenching medium.

THE NEED FOR TESTING

Almost all people have experienced the effects of protective devices operating properly. When an overload or a short circuit occurs in the home, the usual result is a blown fuse or a tripped circuit breaker. Fortunately few have the misfortune to see the results of a defective device, which may include burned wiring, fires, explosions, and electrical shock.

It is often assumed that the fuses and circuit breakers in the home or industry are infallible, and will operate safely when called upon to do so ten, twenty, or more years after their installation. In the case of fuses, this may be a safe assumption, because a defective fuse usually blows too quickly, causing premature opening of the circuit, and forcing replacement of the faulty component. Circuit breakers, however, are mechanical devices, which are subject to deterioration due to wear, corrosion and environmental contamination, any of which could cause the device to remain closed during a fault condition. At the very least, the specified time delay may have shifted so much that proper protection is no longer afforded to devices on the circuit, or improper coordination causes a main circuit breaker or fuse to open in an inconvenient location.
Post: #2
plz give me ppts,documentation on digital testing of high voltage circuit breakers
Post: #3

.pptx  today circuit breaker.pptx (Size: 913.51 KB / Downloads: 437)
Circuit Breaker

presented by By:
Chandramohan S. Jha
Class :- 7th EE
Roll no :- 26.


abstract
Mechanical switching devices capable of making, carrying and breaking currents under normal and abnormal
Post: #4
sir i needed to take a seminar on digital testing of high voltage circuit breakers .so i request you to sent me the full content about this papper
Post: #5


ABSTRACT

The functionality of high-voltage circuit breakers is tested in high-power laboratories. Due to the necessary power and the physical size of the equipment, testing is rather expensive and time consuming. The steps followed so far by the authors in order to enable the digital testing of HV circuit breakers are described in this paper. At the end of the article, examples of digital testing are also presented.

INTRODUCTION.

Electrical Energy, Transients and Circuit Breakers.
With the introduction of alternating current (AC) electrical energy as a versatile power source for every conceivable application by the end of the 19th Century, the problem of transporting and distributing this energy arose /a/. In the case of changing the topology of a power system and protecting against (total) failure, the Circuit Breaker (CB) is an irreplaceable element. Although it is commonly said that: "the circuit breaker opens the circuit", it is in fact the electric-arc (arc for short) formed inside the circuit breaker, which interrupts the circuit current. How the arc is able to interrupt a (short-circuit) current is known through many years of practical experience and from the science of plasma physics e.g. /b,c,d,e,f,g,h,i,j,k/. However, since many energy exchange processes play a role in the extinguishing process of the arc, we are still unable to predict, with a near to 100% probability, whether a (newly built) circuit breaker will interrupt a certain current in a specific circuit. It is for this reason that circuit breakers are put to the test during the design and proving stages. These tests are carried out in so called 'High Power Laboratories' /l/. High Power Laboratories test especially High-Voltage Circuit-Breakers in a separate test circuit, since in-grid-testing would jeopardize normal operations of the power system. Test circuits try to simulate the most conceivable network or circuit conditions /m/. This is quite difficult since the electrical phenomena which occur when a circuit is interrupted are rather complicated and depend on numerous network (and arc) conditions. The most harsh conditions occur when a circuit breaker has to interrupt a short circuit current. At first the breaker is subjected to a high current which heats it up considerably (or the arc for that matter) and by means of the accompanying Lorentz forces parts are put under great mechanical stress. When the breaker interrupts the current (at a natural current zero) the subsequent Transient Recovery Voltage (TRV) subjects the breaker (or former arc channel) to a high dielectric stress. Both phenomena, i.e. the high current and the high (transient) voltage, have to be withstood by the breaker and cannot be avoided in any way.


With the advancement of power system, the lines and other equipment operate at very high voltages and carry large currents. High-voltage circuit breakers play an important role in transmission and distribution systems. A circuit breaker can make or break a circuit, either manually or automatically under all conditions viz. no-load, full-load and short-circuit conditions. The American National Standard Institute (ANSI) defines circuit breaker as: "A mechanical switching device capable of making, carrying and breaking currents under normal circuit conditions and also making, carrying for a specified time, and breaking currents under specified abnormal circuit conditions such as those of short circuit". A circuit breaker is usually intended to operate infrequently, although some types are suitable for frequent operation.

THE NEED FOR TESTING

Almost all people have experienced the effects of protective devices operating properly. When an overload or a short circuit occurs in the home, the usual result is a blown fuse or a tripped circuit breaker. Fortunately few have the misfortune to see the results of a defective device, which may include burned wiring, fires, explosions, and electrical shock.
It is often assumed that the fuses and circuit breakers in the home or industry are infallible, and will operate safely when called upon to do so ten, twenty, or more years after their installation. In the case of fuses, this may be a safe assumption, because a defective fuse usually blows too quickly, causing premature opening of the circuit, and forcing replacement of the faulty component. Circuit breakers, however, are mechanical devices, which are subject to deterioration due to wear, corrosion and environmental contamination, any of which could cause the device to remain closed during a fault condition. At the very least, the specified time delay may have shifted so much that proper protection is no longer afforded to devices on the circuit, or improper coordination causes a main circuit breaker or fuse to open in an inconvenient location.

Fore more:
http://www.adl.nl/phd%20thesis.pdf
http://ieeexplore.ieeeXplore/login.jsp?u...ision=-203
http://www.andhracollegesonline/seminar-...%20Breaker



Post: #6
sir,
i need it's complete seminar repo[/align]rt.
Post: #7
can u send me the report?
Post: #8
to get information about the topic"Digital Testing of High Voltage Circuit Breaker"refer the link bellow

http://project-seminars.com/Thread-digit...it-breaker
Post: #9
to get information about the topic Digital testing of high voltage circuitbreakers full report ,ppt and related topic refer the link bellow
http://project-seminars.com/Thread-digit...it-breaker

http://project-seminars.com/Thread-digit...ker?page=2
Post: #10
sir i need full content on this report so kindly send full content on digital testing of hv circuit breaker
Post: #11
sorry i too dnt am also waiting for that only am also a student
Post: #12
to get information about the topic Digital Testing of High Voltage Circuit Breaker full report ppt and related topic refer the link bellow

http://project-seminars.com/Thread-digit...it-breaker

http://project-seminars.com/Thread-digit...ker?page=2
Post: #13
to get information about the topic "digital testing of high voltage circuit breaker" full report ppt and related topic refer the link bellow

http://project-seminars.com/Thread-digit...it-breaker

http://project-seminars.com/Thread-digit...t-breakers

http://project-seminars.com/Thread-digit...ker?page=2
Post: #14
please send me ppt on digital testing of high voltage circuit breaker
Post: #15
hello sir
i want complete ppt of digital testing of circuit breaker
 

Marked Categories : testing of circuit breakers ppts, digital testing of high voltage circuitbreakers, digi tal testing of high voltage circuit breaker, digital testing of hv circuit breaker, abb high voltage circuit breaker, digital technique of high voltage circuit breake electrical seminar report pdf, digital testing of high voltage circuit breakers in pdf, digital testing of high voltage circuit breaker topic, digital testing of a high voltage circuit breaker, pdf digital testing of high voltage circuit breaker, digital testing of high voltage circuit breaker, digital testing of high voltage circuit breakers, digital testing of high voltage circuit breakers pdf,

[-]
Quick Reply
Message
Type your reply to this message here.

Image Verification
Image Verification
(case insensitive)
Please enter the text within the image on the left in to the text box below. This process is used to prevent automated posts.

Possibly Related Threads...
Thread: Author Replies: Views: Last Post
  seminar report high rise buildings ppt Guest 0 0 Today 12:25 PM
Last Post: Guest
  underground cable fault distance locator circuit diagram Guest 0 0 19-07-2017 09:17 PM
Last Post: Guest
  seminar report high and low voltage cut off delay alarm pdf Guest 0 258 16-07-2017 12:20 AM
Last Post: Guest
  aradhya notes software testing Guest 0 271 16-07-2017 12:20 AM
Last Post: Guest
  pdf of car parking gaurd circuit using ir sensor Guest 0 200 16-07-2017 12:20 AM
Last Post: Guest
  high speed four way hacksaw machine Guest 0 256 16-07-2017 12:20 AM
Last Post: Guest
  flexible power electronic transformer circuit diagram Guest 0 162 16-07-2017 12:20 AM
Last Post: Guest
  flexible power electronic transformer circuit diagram Guest 0 174 16-07-2017 12:20 AM
Last Post: Guest
  pd153 color sensor circuit Guest 0 166 16-07-2017 12:20 AM
Last Post: Guest
Question circuit for farmer friendly solar based electric fence for rural agriculture Guest 0 324 16-07-2017 12:20 AM
Last Post: Guest
This Page May Contain What is Digital Testing of High Voltage Circuit Breaker And Latest Information/News About Digital Testing of High Voltage Circuit Breaker,If Not ...Use Search to get more info about Digital Testing of High Voltage Circuit Breaker Or Ask Here

Options: